My house was built in 1978 before my area was annexed 5 years ago.  Bottom
line-  No inspectors, no city code, I've got 3-wire plugs and 2-wire wiring
on every plug I've checked.

As I understand the situation, the power company runs 240V lines to the
house with a earth ground from the power line transformer and your house to
make to split the 240V into two 120V circuits.  Hopefully, these 120V
circuits have balanced current flow and there is little current flow in the
ground, or neutral lead.

It appears that the neutral (white) wire and the ground (green) wire
eventually meet at the ground rod under your meter base.  Assuming that the
above is true and that I can verify that the white wire REALLY IS connected
to neutral at the circuit breaker panel, can the green screw on the duplex
outlet be corrected directly to the neutral at the socket, to ground both my
anti-static mat and my Weller soldering station?

All opinions welcome.

(If this theory is a loser, then I've got a trip through two walls, a closet
ceiling, and a long attic to run a station ground that I need anyway.  It
was almost 100 north of Dallas today and you could probably roast a
thanksgiving turkey in my attic.  I would prefer that attic trip be in late
fall if possible......................)

NJ5A



<<snip>>
I saw a post a few days ago about this.  I have a table mat with snap on
alligator clip.  I do not have unpainted metal ground.  How exactly do I do
this using a resistor and 3 prong plug ??
73 de Jesse W6JMM

_______________________________________________
Elecraft mailing list
Post to: [hidden email]
You must be a subscriber to post to the list.
Subscriber Info (Addr. Change, sub, unsub etc.):
 http://mailman.qth.net/mailman/listinfo/elecraft   

Help: http://mailman.qth.net/subscribers.htm
Elecraft web page: http://www.elecraft.com

Reply | Threaded
Open this post in threaded view
|

Re: Fw: static ground

N2EY
In a message dated 6/10/06 11:36:48 PM Eastern Daylight Time,
[hidden email] writes:


> As I understand the situation, the power company runs 240V lines to the
> house with a earth ground from the power line transformer and your house to
> make to split the 240V into two 120V circuits.  Hopefully, these 120V
> circuits have balanced current flow and there is little current flow in the
> ground, or neutral lead.

Not exactly.

The power co. distribution transformer has a center tapped secondary. That
center tap is the neutral, and it has the same current rating as the two 'hot'
wires.
 
>
> It appears that the neutral (white) wire and the ground (green) wire
> eventually meet at the ground rod under your meter base.

Sort of. They are supposed to be connected at the 'service entrance'.
Usually, that's the panel with the main breaker.

The neutral is also grounded at the transformer, but that's the power
company's domain.

The *only* place in your house that neutral should be connected to ground is
at the service entrance.

 Assuming that the
>
> above is true and that I can verify that the white wire REALLY IS connected
> to neutral at the circuit breaker panel, can the green screw on the duplex
> outlet be corrected directly to the neutral at the socket, to ground both my
>
> anti-static mat and my Weller soldering station?
>

I wouldn't do that.

National Electrical Code specifically states not to do that. The neutral lead
(known colloquially as the 'white wire') is not a grounding conductor. That's
why a third wire (bare or green) is run - the bare wire is the ground wire.

I find it odd that such a new house doesn't have ground wires. Are the boxes
and faceplates metal? If so, there should be some form of grounding.

One way to test is to make a "test light" of a low-wattage 110 volt bulb and
two test leads, and see if the faceplate is grounded by connecting it between
the hot prong and the metal faceplate of the outlet. (BE SURE TO TAKE ALL
NECESSARY PRECAUTIONS!!) If the lamp works, the faceplate is already grounded. A
lamp is used, rather than a meter, to prove that the ground can handle some
current.

73 de Jim, N2EY

_______________________________________________
Elecraft mailing list
Post to: [hidden email]
You must be a subscriber to post to the list.
Subscriber Info (Addr. Change, sub, unsub etc.):
 http://mailman.qth.net/mailman/listinfo/elecraft   

Help: http://mailman.qth.net/subscribers.htm
Elecraft web page: http://www.elecraft.com

Reply | Threaded
Open this post in threaded view
|

RE: Fw: static ground

Don Wilhelm-3
In reply to this post by Bob Robertson-5
While it is true that the white wire does connect to ground at the service
entrance, that wire should not be considered a ground because it is a
current carrying conductor.  Figure the voltage drop in one ohm of wire
carrying 15 amps - that will produce 15 volts - and that voltage is what
makes the white wire 'not a ground'.  Additionally, if the white conductor
should open at some point between your connection point and the service
panel, it can become 'hot' with full line voltage on it.  With the sloppy
way I have seen some electrical connections done, the possibility of an open
circuit is quite high.

Re-wiring your home may not be practical at this point (but it would be a
wise step), but it would be practical to run a wire from critical places
such as the ham shack or the workbench area to the service entrance ground
as an added safety ground wire.  If you use a separate ground for the shack,
that ground should also connect back to the utility service entrance
(connect your added safety ground wire to the shack ground).

Remember that your safety is at stake anytime you plug an appliance with a 3
prong plug into one of your ungrounded sockets.  There is no protection if
the appliance should develop an internal fault.

73,
Don W3FPR


> -----Original Message-----
>
> My house was built in 1978 before my area was annexed 5 years
> ago.  Bottom
> line-  No inspectors, no city code, I've got 3-wire plugs and
> 2-wire wiring
> on every plug I've checked.
>
>

_______________________________________________
Elecraft mailing list
Post to: [hidden email]
You must be a subscriber to post to the list.
Subscriber Info (Addr. Change, sub, unsub etc.):
 http://mailman.qth.net/mailman/listinfo/elecraft   

Help: http://mailman.qth.net/subscribers.htm
Elecraft web page: http://www.elecraft.com

Reply | Threaded
Open this post in threaded view
|

RE: static ground

Steven Pituch
In reply to this post by Bob Robertson-5
Hi Bob,
Sounds like you live in Texas.

Your theory is pretty much correct.  I am a professional Engineer,  and home
inspector in Texas.   The default way to deal with (update) a two wire
circuit is to install a GFCI in the upstream outlet and slave the GFCI to
the downstream outlets. However if there is not a ground available in the
box, you must label the outlet "No Equipment Ground".

I haven't found the Lutron PDF file on their site that I use as reference,
but I found an abbreviated explaination here:
See:  http://www.codecheck.com/250_50_commentary.html

Its very possible that the center screw and the box may not be grounded.  If
it isn't do not connect the ground screw on the outlet to the neutral.  

The NEC code is quite confusing.  If you need to determine a grounding
method I can look it up, but I am sure its not going to be simple.

If it’s the first floor it might be best to just drive a ground rod into the
earth for your RF and static ground and not wire it directly to the
electrical system.

Regards,
Steve, W2MY

--
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.1.394 / Virus Database: 268.8.3/360 - Release Date: 6/9/2006
 

_______________________________________________
Elecraft mailing list
Post to: [hidden email]
You must be a subscriber to post to the list.
Subscriber Info (Addr. Change, sub, unsub etc.):
 http://mailman.qth.net/mailman/listinfo/elecraft   

Help: http://mailman.qth.net/subscribers.htm
Elecraft web page: http://www.elecraft.com

Reply | Threaded
Open this post in threaded view
|

RE: Fw: static ground

Ron D'Eau Claire-2
In reply to this post by Don Wilhelm-3
That's also why the anti-static ground has (must have!) a 1-megohm resistor
in series with it. That way a dangerous amount of current isn't going to
flow in any case while the resistance is still low enough to continuously
dissipate any static charges that are developed. It doesn't matter whether
you accidentally come in contact with the "hot" side of a mains lead or the
positive side of some other power source, the resistor should keep the
current down to safe levels.

So, if you have nothing else, any connection to the earth will work either
as a terminal for the anti static pad/strap with their internal 1 meg
resistors or as a point you can touch briefly (while not touching anything
else) to dissipate any charge on your body just before you handle a static
sensitive part.

Don makes a good point about running a ground wire through the house, at
least to the critical outlets near the ham shack. I'd include, as a minimum,
kitchen and bath outlets as well so they can be equipped with ground-fault
interrupters. I 'grew up' in the age of exposed AC/DC equipment that had one
side of the metal case connected to the mains, and I recall many instances
of touching a panel and noting the slight tingle that warned me that I was
touching the hot side of the mains line because the plug was in backwards.
That was a warning because the next metal panel a few inches away might be
grounded and touching both of them at once would put me across the mains
power! Millions of people survived such wiring without problem, but many did
die. Don't be one of them.

Ron AC7AC

_______________________________________________
Elecraft mailing list
Post to: [hidden email]
You must be a subscriber to post to the list.
Subscriber Info (Addr. Change, sub, unsub etc.):
 http://mailman.qth.net/mailman/listinfo/elecraft   

Help: http://mailman.qth.net/subscribers.htm
Elecraft web page: http://www.elecraft.com

Reply | Threaded
Open this post in threaded view
|

Re: Fw: static ground

David A. Belsley
In reply to this post by Don Wilhelm-3
Bob:
   Your old house wiring may be BX, meaning it is wire in a spiral  
armored casing, typically made of aluminum.  While not ideal, you may  
be able to gain an independent ground using this casing.  It would  
require (a) that the casing be continuous from receptacle to  
receptacle, and (b) that it be well clamped with a BX connector to  
each receptacle.  In this case, you can add 3-prong plugs with ground  
wires firmly connected (under a screw head, for example) to the  
receptacle.   Once you do this, you can get a "tester plug" from you  
local jobber or hardware that can be used to determine whether all is  
well.  These tester plugs indicate with lights whether the polarity  
is correct, the common is closed, and the ground exists.

best wishes,

dave belsley, w1euy



On Jun 11, 2006, at 8:24 AM, Don Wilhelm wrote:

> While it is true that the white wire does connect to ground at the  
> service
> entrance, that wire should not be considered a ground because it is a
> current carrying conductor.  Figure the voltage drop in one ohm of  
> wire
> carrying 15 amps - that will produce 15 volts - and that voltage is  
> what
> makes the white wire 'not a ground'.  Additionally, if the white  
> conductor
> should open at some point between your connection point and the  
> service
> panel, it can become 'hot' with full line voltage on it.  With the  
> sloppy
> way I have seen some electrical connections done, the possibility  
> of an open
> circuit is quite high.
>
> Re-wiring your home may not be practical at this point (but it  
> would be a
> wise step), but it would be practical to run a wire from critical  
> places
> such as the ham shack or the workbench area to the service entrance  
> ground
> as an added safety ground wire.  If you use a separate ground for  
> the shack,
> that ground should also connect back to the utility service entrance
> (connect your added safety ground wire to the shack ground).
>
> Remember that your safety is at stake anytime you plug an appliance  
> with a 3
> prong plug into one of your ungrounded sockets.  There is no  
> protection if
> the appliance should develop an internal fault.
>
> 73,
> Don W3FPR
>
>
>> -----Original Message-----
>>
>> My house was built in 1978 before my area was annexed 5 years
>> ago.  Bottom
>> line-  No inspectors, no city code, I've got 3-wire plugs and
>> 2-wire wiring
>> on every plug I've checked.
>>
>>
>
> _______________________________________________
> Elecraft mailing list
> Post to: [hidden email]
> You must be a subscriber to post to the list.
> Subscriber Info (Addr. Change, sub, unsub etc.):
>  http://mailman.qth.net/mailman/listinfo/elecraft
>
> Help: http://mailman.qth.net/subscribers.htm
> Elecraft web page: http://www.elecraft.com

-------------------------------------
david a. belsley
professor of economics

_______________________________________________
Elecraft mailing list
Post to: [hidden email]
You must be a subscriber to post to the list.
Subscriber Info (Addr. Change, sub, unsub etc.):
 http://mailman.qth.net/mailman/listinfo/elecraft   

Help: http://mailman.qth.net/subscribers.htm
Elecraft web page: http://www.elecraft.com

Reply | Threaded
Open this post in threaded view
|

RE: static ground

Steven Pituch
In reply to this post by Ron D'Eau Claire-2
Hi Ron and all,
Actually the name GFCI is a bit misleading I think.  You don't need a ground
for a GFCI to work.  That's why they recommend their use in upgrading two
wire systems.  The GFCI senses a current difference between the neutral and
the hot wire.  If the difference is greater than 5 milliamps, the GFCI is
supposed to trip and disable the circuit.  Thus if you get a shock and the
GFCI trips you were in essence the "ground fault" in "Ground Fault Circuit
Interupter".  Having a third wire as ground is nice to have, but it seems
that putting a GFCI in a two wire circuit greatly increases the safety of
the circuit.

Steve, W2MY

-----Original Message-----
From: [hidden email]
[mailto:[hidden email]] On Behalf Of Ron D'Eau Claire

Don makes a good point about running a ground wire through the house, at
least to the critical outlets near the ham shack. I'd include, as a minimum,
kitchen and bath outlets as well so they can be equipped with ground-fault
interrupters.

--
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.1.394 / Virus Database: 268.8.3/360 - Release Date: 6/9/2006
 