Grounding

classic Classic list List threaded Threaded
8 messages Options
Reply | Threaded
Open this post in threaded view
|

Grounding

Jim Brown-10
On Sun,9/27/2015 10:37 PM, Fred Townsend wrote:
>
>
>   > Often the requirements of one system will be at odds with other >
> grounding requirements. For instance you generally want a high >
> impedance for RFI issues and a very low impedance for lightning >
> grounds. One system defeats the other so they really need to be
> separate systems.

> NO, NO, NO, NO!
>
>    [Fred Townsend] Well yes maybe. How do you bond a ferrite choke?
> Are not all chokes high impedance at their intended useful frequency?
> I said 'system' not 'ground'.
>
> [K9YC]
>
> Huh? Chokes are used on SIGNAL lines, NOT on bonding conductors. A
> fundamental requirement of bonding is that it be LOW IMPEDANCE, so, in
> general, bonding conductors should not be choked. Further, lightning
> is NOT a DC event, it is an RF event. It's an impulse, with broad
> energy peak around 1 MHz.
>
> [Fred Townsend] Correct on all scores
> Jim I think you have tunnel vision on bonding. Jim as others suggested
> this was really an EMI issue and I was addressing this as a system or
> EMI issue.

The bonding methods I have outlined in my tutorial are specifically
designed to satisfy both EMI and lightning protection. Proper bonding
for NEC is NOT in conflict with noise free operation of ANY system,
whether it be audio, video, or radio.

> In this case chokes are appropriate for signal AND power cords
> containing neutral. I don't believe anyone suggested chokes on bonding
> conductors. However you suggested everything should be bonded and I
> merely asked how you bond a choke.

I said that ALL GROUNDS and GROUNDED equipment must be bonded together.
A choke is neither.

Signal cables and power cables are NOT bonding conductors.  Bonding
refers to those conductors that provide a dedicated, robust, low
impedance connection between all grounded elements of premises wiring.
Bonding conductors are those which connect together all equipment in a
station, all earth electrodes in a premises. This includes but is not
limited to the EARTH connections for CATV, Telco, satellite dishes,
mains power. It also includes those used for antennas where they enter a
premises.  In simple terms, NEC (and the laws of physics) allow as many
earth electrodes as we want, but they MUST all be bonded together.

> Also the NEC as well as other codes prohibit tying neutral and safety
> (green wire) together.

Not quite!  NEC REQUIRES that neutral and green be bonded together at
one, and ONLY one point in every SYSTEM, and, in general, requires that
the bond be very close to the point where the system is established.  
[The word "system" here specifically refers to the wiring that
distributes power in a facility, and to equipment connected to it.]  A
"system" is established when the power enters a premises, and a bond is
required there. In most premises, that's the only system. A system is
also established by a transformer, as might be used in large buildings
to run large loads, and by equipment like a UPS. In both examples, this
does NOT require a new earth electrode, but rather a bond between
neutral and green at that point.

The correct part of your statement is that NEC prohibits tying neutral
and safety (green) together any place OTHER than where the system is
established.

> Two cases I called out in my four different parts of the system. So no
> you do not tie all grounds together.

You misunderstand the concepts. See the above.  All grounds MUST be
bonded together.

Another important distinction -- a cable shield is not "grounded," and
there is no virtue in doing so EXCEPT for lightning protection. The
shield is properly connected to the shielding enclosure at each simply
to make SHIELDING continuous, and thus make it effective. This is not a
GROUND, it is a SHIELD connection. And in an unbalanced circuit (where
the shield is the signal return), it is also signal return.

When we add a common mode choke to an antenna downlead, we are
preventing common mode current on the cable shield. We bond the antenna
shield to ground at the point of entry, and we bond that point of entry
to a the building ground, but that is to protect the premises, NOT the
antenna.  That cable shield is NOT a ground, it is a shield, and it is a
signal return. That would work with a coax feedthrough, but it would not
protect a rig connected to the antenna. To do that, we replace the
feedthrough with a Polyphaser, which shorts the center conductor to the
shield in the event of a strike.

Again, I strongly urge you and others who want to understand these
concepts to study the links on my website, previously cited. Members of
the AES Standards Committee Working Group on EMC spent YEARS in
discussions that ultimately led to the understandings I've articulated.
The members of the WG are all engineers, most with very broad background
in everything from power systems to broadcasting to recording to live
sound to RF systems. They included engineers from the BBC, ABC-TV, sound
system consultants, equipment manufacturers, and contractors. Many
are/were hams.

> Furthermore I think the whole issue of grounding is exacerbated by the
> overuse and incorrect use of the word 'ground'.

I absolutely agree, and I've preached that for years. I wrote material
on exactly that for the ARRL Handbook, and it was rejected.

> The Brits prefer to use the word 'earth' which helps a little.

Only a little -- they use "earth" and "earthing" in the same manner that
we use "ground" and "grounding" in North America, and they talk about a
"Protective Earth Conductor" which corresponds roughly to our "green
wire." I serve on the AES Standards Committee with these folks. Good
people, but they talk just as funny as we do.

> I would prefer to bury the word 'ground' and replace it with context
> appropriate words like 'signal common' but that isn't common practice.

It should be, and I have been doing that for years. There are, at least,
four common uses of the word "ground" to describe very different things.
I have long preached that the words "ground" and "balun" should be
erased from all literature, because they do far more to confuse us than
enlighten us.

And this question remains. When I spend MONTHS writing a tutorial on
stuff like this, and post a link to it in response to someone who
obviously needs to study it, why is it that the person won't take the
time to read what I have taken pains to write for their benefit?
Instead, we burden the thousand or so readers of this list with a long
response that should not be necessary.

73, Jim K9YC
______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[hidden email]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to [hidden email]
Reply | Threaded
Open this post in threaded view
|

Re: Grounding

Mike Reublin NF4L
Jim -

The discussions are not a burden at all. I enjoy them immensely, and consider them a valuable resource for my education. Please dont be annoyed.

73, Mike NF4L
> On Sep 28, 2015, at 12:37 PM, Jim Brown <[hidden email]> wrote:
>
> And this question remains. When I spend MONTHS writing a tutorial on stuff like this, and post a link to it in response to someone who obviously needs to study it, why is it that the person won't take the time to read what I have taken pains to write for their benefit? Instead, we burden the thousand or so readers of this list with a long response that should not be necessary.
>
> 73, Jim K9YC
> ___________
______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[hidden email]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to [hidden email]
Reply | Threaded
Open this post in threaded view
|

Re: Grounding

ktalbott
In reply to this post by Jim Brown-10
Tried direct response but Mr. Brown doesn't accept email from just anyone.

Several years ago the NEC relaxed the requirement that safety ground and
neutral be connected at only one place.  Now you may leave the bonding screw
in place in remote panels.

Ken - ke4rg

-----Original Message-----
From: [hidden email]
[mailto:[hidden email]] On Behalf Of Jim Brown
Sent: Monday, September 28, 2015 12:37 PM
To: Reflector Elecraft
Subject: [Elecraft] Grounding

On Sun,9/27/2015 10:37 PM, Fred Townsend wrote:
>
>
>   > Often the requirements of one system will be at odds with other >
> grounding requirements. For instance you generally want a high >
> impedance for RFI issues and a very low impedance for lightning >
> grounds. One system defeats the other so they really need to be
> separate systems.

> NO, NO, NO, NO!
>
>    [Fred Townsend] Well yes maybe. How do you bond a ferrite choke?
> Are not all chokes high impedance at their intended useful frequency?
> I said 'system' not 'ground'.
>
> [K9YC]
>
> Huh? Chokes are used on SIGNAL lines, NOT on bonding conductors. A
> fundamental requirement of bonding is that it be LOW IMPEDANCE, so, in
> general, bonding conductors should not be choked. Further, lightning
> is NOT a DC event, it is an RF event. It's an impulse, with broad
> energy peak around 1 MHz.
>
> [Fred Townsend] Correct on all scores
> Jim I think you have tunnel vision on bonding. Jim as others suggested
> this was really an EMI issue and I was addressing this as a system or
> EMI issue.

The bonding methods I have outlined in my tutorial are specifically designed
to satisfy both EMI and lightning protection. Proper bonding for NEC is NOT
in conflict with noise free operation of ANY system, whether it be audio,
video, or radio.

> In this case chokes are appropriate for signal AND power cords
> containing neutral. I don't believe anyone suggested chokes on bonding
> conductors. However you suggested everything should be bonded and I
> merely asked how you bond a choke.

I said that ALL GROUNDS and GROUNDED equipment must be bonded together.
A choke is neither.

Signal cables and power cables are NOT bonding conductors.  Bonding refers
to those conductors that provide a dedicated, robust, low impedance
connection between all grounded elements of premises wiring.
Bonding conductors are those which connect together all equipment in a
station, all earth electrodes in a premises. This includes but is not
limited to the EARTH connections for CATV, Telco, satellite dishes, mains
power. It also includes those used for antennas where they enter a premises.
In simple terms, NEC (and the laws of physics) allow as many earth
electrodes as we want, but they MUST all be bonded together.

> Also the NEC as well as other codes prohibit tying neutral and safety
> (green wire) together.

Not quite!  NEC REQUIRES that neutral and green be bonded together at one,
and ONLY one point in every SYSTEM, and, in general, requires that the bond
be very close to the point where the system is established.  
[The word "system" here specifically refers to the wiring that distributes
power in a facility, and to equipment connected to it.]  A "system" is
established when the power enters a premises, and a bond is required there.
In most premises, that's the only system. A system is also established by a
transformer, as might be used in large buildings to run large loads, and by
equipment like a UPS. In both examples, this does NOT require a new earth
electrode, but rather a bond between neutral and green at that point.

The correct part of your statement is that NEC prohibits tying neutral and
safety (green) together any place OTHER than where the system is
established.

> Two cases I called out in my four different parts of the system. So no
> you do not tie all grounds together.

You misunderstand the concepts. See the above.  All grounds MUST be bonded
together.

Another important distinction -- a cable shield is not "grounded," and there
is no virtue in doing so EXCEPT for lightning protection. The shield is
properly connected to the shielding enclosure at each simply to make
SHIELDING continuous, and thus make it effective. This is not a GROUND, it
is a SHIELD connection. And in an unbalanced circuit (where the shield is
the signal return), it is also signal return.

When we add a common mode choke to an antenna downlead, we are preventing
common mode current on the cable shield. We bond the antenna shield to
ground at the point of entry, and we bond that point of entry to a the
building ground, but that is to protect the premises, NOT the antenna.  That
cable shield is NOT a ground, it is a shield, and it is a signal return.
That would work with a coax feedthrough, but it would not protect a rig
connected to the antenna. To do that, we replace the feedthrough with a
Polyphaser, which shorts the center conductor to the shield in the event of
a strike.

Again, I strongly urge you and others who want to understand these concepts
to study the links on my website, previously cited. Members of the AES
Standards Committee Working Group on EMC spent YEARS in discussions that
ultimately led to the understandings I've articulated.
The members of the WG are all engineers, most with very broad background in
everything from power systems to broadcasting to recording to live sound to
RF systems. They included engineers from the BBC, ABC-TV, sound system
consultants, equipment manufacturers, and contractors. Many are/were hams.

> Furthermore I think the whole issue of grounding is exacerbated by the
> overuse and incorrect use of the word 'ground'.

I absolutely agree, and I've preached that for years. I wrote material on
exactly that for the ARRL Handbook, and it was rejected.

> The Brits prefer to use the word 'earth' which helps a little.

Only a little -- they use "earth" and "earthing" in the same manner that we
use "ground" and "grounding" in North America, and they talk about a
"Protective Earth Conductor" which corresponds roughly to our "green wire."
I serve on the AES Standards Committee with these folks. Good people, but
they talk just as funny as we do.

> I would prefer to bury the word 'ground' and replace it with context
> appropriate words like 'signal common' but that isn't common practice.

It should be, and I have been doing that for years. There are, at least,
four common uses of the word "ground" to describe very different things.
I have long preached that the words "ground" and "balun" should be erased
from all literature, because they do far more to confuse us than enlighten
us.

And this question remains. When I spend MONTHS writing a tutorial on stuff
like this, and post a link to it in response to someone who obviously needs
to study it, why is it that the person won't take the time to read what I
have taken pains to write for their benefit?
Instead, we burden the thousand or so readers of this list with a long
response that should not be necessary.

73, Jim K9YC
______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[hidden email]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html Message
delivered to [hidden email]

______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[hidden email]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to [hidden email]
Reply | Threaded
Open this post in threaded view
|

Re: Grounding

Jim Brown-10
On Mon,9/28/2015 11:26 AM, Kenneth Talbott wrote:
> Several years ago the NEC relaxed the requirement that safety ground and
> neutral be connected at only one place.  Now you may leave the bonding screw
> in place in remote panels.

NO! NO! NO!

73, Jim K9YC
______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[hidden email]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to [hidden email]
Reply | Threaded
Open this post in threaded view
|

Re: Grounding

Alan Bloom
On 09/28/2015 01:19 PM, Jim Brown wrote:
> On Mon,9/28/2015 11:26 AM, Kenneth Talbott wrote:
>> Several years ago the NEC relaxed the requirement that safety ground and
>> neutral be connected at only one place.  Now you may leave the bonding
>> screw
>> in place in remote panels.
>
> NO! NO! NO!

Literally as we speak, there is an electrician outside in the middle of
a major re-wiring job at my house.  So I asked him and he said that
under certain conditions the NEC does allow grounding the neutral wire
in an outbuilding.

In my case, he is not doing that in my outbuilding.  He says it is
always better to tie neutral and ground only at the service entrance if
possible.

Alan N1AL
______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[hidden email]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to [hidden email]
Reply | Threaded
Open this post in threaded view
|

Re: Grounding

Jim Brown-10
In reply to this post by ktalbott
On Mon,9/28/2015 11:26 AM, Kenneth Talbott wrote:
> Several years ago the NEC relaxed the requirement that safety ground and
> neutral be connected at only one place.  Now you may leave the bonding screw
> in place in remote panels.

http://ecmweb.com/code-basics/grounding-and-bonding-part-2-3

The link above is from Mike Holt, widely considered an authority on
electrical codes. He makes his living teaching and writing about the
topic. This is part of his review of revisions to Article 250, Grounding
and Bonding, that appeared in the 2011 code. In the very last paragraph,
are these words:

"As a rule, the neutral should never be connected to the enclosure or
equipment grounding conductor anywhere except in the service disconnects
and the secondary side of separately derived systems. Objectionable
neutral current presents a real danger and can damage equipment as well
as cause fires and electric shock or electrocution."

For all practical purposes, the 2011 code is the most recent, because it
usually takes 5-6 years for local authorities to adopt a revision.  Upon
reading your email, I reviewed a draft of the 2014 code, and the
requirement for one, and only one, neutral to ground bond is still part
of it.

The only "remote panel" in which a bond would be permitted between
neutral and ground is one in a second building where ground is not
carried between buildings, or when the remote panel is for a "separately
derived system." A system is separately derived when fed by a
transformer. The practice of not carrying ground between buildings no
longer permitted, but is grandfathered in existing installations from
earlier versions of NEC.

73, Jim K9YC

______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[hidden email]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to [hidden email]
Reply | Threaded
Open this post in threaded view
|

Re: Grounding

ktalbott
Yes NEC 2008 250.32B EXCEPTION is that to which I refer

When the debate is lost, slander becomes the tool of the loser.   Socrates


-----Original Message-----
From: [hidden email]
[mailto:[hidden email]] On Behalf Of Jim Brown
Sent: Monday, September 28, 2015 5:30 PM
To: Reflector Elecraft
Subject: Re: [Elecraft] Grounding

On Mon,9/28/2015 11:26 AM, Kenneth Talbott wrote:
> Several years ago the NEC relaxed the requirement that safety ground
> and neutral be connected at only one place.  Now you may leave the
> bonding screw in place in remote panels.

http://ecmweb.com/code-basics/grounding-and-bonding-part-2-3

The link above is from Mike Holt, widely considered an authority on
electrical codes. He makes his living teaching and writing about the topic.
This is part of his review of revisions to Article 250, Grounding and
Bonding, that appeared in the 2011 code. In the very last paragraph, are
these words:

"As a rule, the neutral should never be connected to the enclosure or
equipment grounding conductor anywhere except in the service disconnects and
the secondary side of separately derived systems. Objectionable neutral
current presents a real danger and can damage equipment as well as cause
fires and electric shock or electrocution."

For all practical purposes, the 2011 code is the most recent, because it
usually takes 5-6 years for local authorities to adopt a revision.  Upon
reading your email, I reviewed a draft of the 2014 code, and the requirement
for one, and only one, neutral to ground bond is still part of it.

The only "remote panel" in which a bond would be permitted between neutral
and ground is one in a second building where ground is not carried between
buildings, or when the remote panel is for a "separately derived system." A
system is separately derived when fed by a transformer. The practice of not
carrying ground between buildings no longer permitted, but is grandfathered
in existing installations from earlier versions of NEC.

73, Jim K9YC

______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[hidden email]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html Message
delivered to [hidden email]

______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[hidden email]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to [hidden email]
Reply | Threaded
Open this post in threaded view
|

Re: Grounding

Eric Swartz - WA6HHQ
Administrator
Folks - This is now treading into more personal comments. We're also past the
limit for single, slightly off-topic, postings. Thread closed.

Please keep it polite and respectful, as if having a pleasant get together with
friends in your living room face to face.

73,
Eric
List Moderator
/elecraft.com/

On 9/28/2015 2:45 PM, Kenneth Talbott wrote:
> Yes NEC 2008 250.32B EXCEPTION is that to which I refer
>
> When the debate is lost, slander becomes the tool of the loser.   Socrates
>
>
______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[hidden email]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to [hidden email]